Lawrence Duckworth 03-20-2011 08:16 PM

I really don’t know much more than that I need a single phase 50 kva 4 to 1 step down (whatever the heck that means)…does this look like the ideal transformer for a 200 elbeerer?

Dennis Hetland 03-20-2011 10:47 PM

This appears to be a 4to1/2to1 step down transformer. You're not showing the entire nameplate There's more info on it, like the KVA.
I can't be 1000% positive, but I'm assuming this is rated for 480v on the primary. If you have a 240v service going to your primary and you wire X1 to X3 and X2 to X4 you should get 60v out of your secondary.
The 1 through 6 on the primary are taps for adjusting to high or low voltage coming from your service. Like if you're supposed to have a 480v service, but you're actually getting 500v you can tap it so your secondary is putting out the proper voltage. You could play with those taps to get slightly more or less than 60 volts. If you wanted to for some reason.
You should post another picture that shows the entire nameplate.

Charles Friedman 03-20-2011 10:50 PM

So, I was just wondering what the intended use of this furnace? At this point in construction and placement of this object that is going to be the warehouse of a marketable commodity, I would be thinking about putting a scale under this unit, as well as an adjustable height and leveling mechanism.
Just a thought.

Pete VanderLaan 03-21-2011 05:18 AM

And what you want is sixty volts run with a single bank of five of the elements we'll provide wired in series.

Lawrence Duckworth 03-21-2011 08:23 AM

Quote:

Originally Posted by Dennis Hetland (Post 95267)
This appears to be a 4to1/2to1 step down transformer. You're not showing the entire nameplate There's more info on it, like the KVA.
I can't be 1000% positive, but I'm assuming this is rated for 480v on the primary. If you have a 240v service going to your primary and you wire X1 to X3 and X2 to X4 you should get 60v out of your secondary.
The 1 through 6 on the primary are taps for adjusting to high or low voltage coming from your service. Like if you're supposed to have a 480v service, but you're actually getting 500v you can tap it so your secondary is putting out the proper voltage. You could play with those taps to get slightly more or less than 60 volts. If you wanted to for some reason.
You should post another picture that shows the entire nameplate.

Dennis that’s it for the photos, but is the bottom line a transformer that puts out 60 volt from a 200 amp single phase service? Is this what I ask for at the sales counter?

> this deal has 6 molly tubes, 240 single phase power <

Pete VanderLaan 03-21-2011 11:11 AM

No. The transformer, assuming it is the correct unit would have an input of 480V. That would break it down to two 240V taps and a 120V tap, plus the correcting taps. You however are going to run 240V in to the thing and it can't perceive the difference between 480 and 240, so it is going to give you two 120V taps and a sixty volt tap instead. You are looking for the sixty.

So you are looking conventionally for a 50KVA transformer 480 volt input with three taps for 240 and 120 secondary outputs. It may have adjusting taps as well.

Or you can custom order a transformer with 240 volt input and 36 volt secondary output through either me or a local supplier, I don't know what your deal is there. I use the 36 volt in my furnace. That works out to two banks of three elements at 12V if wired in series.

Dennis Hetland 03-21-2011 11:25 AM

Exactly what you want is not common so it's likely to cost a lot, but a 480v to 240/120v is common. If you put 240v to the primary of a 480v transformer you'll get 120/60v out of the secondary. If the load on your secondary is 200 amps you'll draw 50 amps from your panel to you primary.(If the secondary is wired for 60v).
A 50KVA 4 to 1 stepdown transformer rated for 480volts on the the primary should work for you.
I should point out that while I have installed transformers I have not built a moly furnace yet. I think it would be worth the money to pay someone like Cheyenne Malcolm for some advice. Especially if you don't have a lot of experience with electrical installations. I'm sure he could tell you where to get the best transformer for your money.

Dennis Hetland 03-21-2011 11:30 AM

Yeah. What Pete said.
(I need to learn to type faster.)

Dennis Hetland 03-21-2011 11:38 AM

Quote:

Originally Posted by Pete VanderLaan (Post 95275)
No. The transformer, assuming it is the correct unit would have an input of 480V. That would break it down to two 240V taps and a 120V tap, plus the correcting taps. You however are going to run 240V in to the thing and it can't perceive the difference between 480 and 240, so it is going to give you two 120V taps and a sixty volt tap instead. You are looking for the sixty.

So you are looking conventionally for a 50KVA transformer 480 volt input with three taps for 240 and 120 secondary outputs. It may have adjusting taps as well.

Or you can custom order a transformer with 240 volt input and 36 volt secondary output through either me or a local supplier, I don't know what your deal is there. I use the 36 volt in my furnace. That works out to two banks of three elements at 12V if wired in series.

What about welders? I thought I heard something about people using welders for their transformers.

Larry Cazes 03-21-2011 12:13 PM

Quote:

Originally Posted by Dennis Hetland (Post 95279)
What about welders? I thought I heard something about people using welders for their transformers.

A welder is NOT a transformer. Most are not designed or built for 100% duty cycle meaning 24 hours/day. We have EZTherm furnaces at the shop I rent at. They use Miller welders. I would not suggest you go there.

Pete VanderLaan 03-21-2011 03:11 PM

Quote:

Originally Posted by Dennis Hetland (Post 95279)
What about welders? I thought I heard something about people using welders for their transformers.

***************
When EZ Therm built their shortlived moly, a cooperative adventure between Henry Halem and Mark Jesson from Duralite, they asked Miller for a welder that would perform continuous duty. Miller said "sure" and supplied them with a unit that supplied continuous duty- for an eight hour work shift. This was an exceptionally unfortunate miscalculation and speaks volumes for testing a product for a year before it gets put on the market. It was only one of many problems.

Use a transformer, a real one.

Larry Cazes 03-21-2011 05:55 PM

Quote:

Originally Posted by Pete VanderLaan (Post 95282)
***************
When EZ Therm built their shortlived moly, a cooperative adventure between Henry Halem and Mark Jesson from Duralite, they asked Miller for a welder that would perform continuous duty. Miller said "sure" and supplied them with a unit that supplied continuous duty- for an eight hour work shift. This was an exceptionally unfortunate miscalculation and speaks volumes for testing a product for a year before it gets put on the market. It was only one of many problems.

Use a transformer, a real one.

Yup. Even the user guide shows 100% duty cycle is actually 8 hours instead of 24 as most would assume. Specsmanship at it's best.

Pete VanderLaan 03-21-2011 06:52 PM

And I would note: Take care of your transformer or it won't last forever either.

Lawrence Duckworth 03-22-2011 12:11 PM

You guys have helped….thanks







Progress--- :)

Rick Sherbert 03-22-2011 12:37 PM

Quote:

Originally Posted by Pete VanderLaan (Post 95265)
I am very sure the Bowman stuff is sold and it was 208 volt three phase anyway. I would look with local demolition contractors in the Atlanta area.

Check is on the way to Jim as we speak:)

Pete VanderLaan 03-22-2011 02:07 PM

Quote:

Originally Posted by Lawrence Duckworth (Post 95294)
You guys have helped….thanks







Progress--- :)

I still think the floor could use more insulation.

Lawrence Duckworth 03-22-2011 08:42 PM

Quote:

Originally Posted by Pete VanderLaan (Post 95297)
I still think the floor could use more insulation.

I finished up with the wall castings and the sill height ended up being 2’-6” off the floor. Is that height worth compromising by adding additional insulation?….

Btw, is the pot lip higher, lower or level with the sill?

Pete VanderLaan 03-23-2011 04:18 AM

a tiny bit lower is best but put the pot on a stilt that completely supports it.

Mark Wilson 03-23-2011 05:31 AM

if a transformer is designed for an input of 480 volts and has a 50 kva output power, and then is used with 240 volts, it now can only supply 12.5 kva or only 25% of the power it could before. the size of the wire used in the transformer is the limiting factor.

Steve Stadelman 03-23-2011 10:10 AM

Quote:

Originally Posted by Mark Wilson (Post 95312)
if a transformer is designed for an input of 480 volts and has a 50 kva output power, and then is used with 240 volts, it now can only supply 12.5 kva or only 25% of the power it could before. the size of the wire used in the transformer is the limiting factor.

No, 25 kva. Redo your math.

Mark Wilson 03-23-2011 01:26 PM

Quote:

Originally Posted by Steve Stadelman (Post 95319)
No, 25 kva. Redo your math.

off by a factor of 2.....the story of my life!!!!

Pete VanderLaan 03-23-2011 03:21 PM

Christine Lavin has this great song called " Don't Push Send."

Lawrence Duckworth 03-25-2011 08:42 PM

Steve S. recommended a 15kva 240 input, 45v output single phase transformer with standard 5% and 10% voltage compensation taps.

Do you guys plug the cleanout with brick and fiber? :confused:

Tim Bassett 03-26-2011 01:22 AM

My stadelman has a layer or two of hot face fibre close to the crucible and then a few layers of standard fibre to back it up. I would not suggest using bricks in case you do need to do a big cleanout. The worst case scenario is that the fibre can never be actually "glued" on place by the glass, you can always shred it and pull it out. I would hate to have to shred a brick that has been glued in place. Hopefully you will have to use the cleanout port very infrequently. I opened my cleanout port after charging at least weekly for 18 months and was surprised that there seemed to be so much glass on the floor...maybe 1/2 an inch. I spent quite a while gathering it all off the floor and it added up to be about three kilos. Best of luck with your build
Tim Bassett

Rollin Karg 03-26-2011 04:52 AM

If you want your furnace to run efficiently for a long time you should clean the bottom out on a regular schedule. At least once a month if not every other week.