replacing MDR with SSR

Since my shows have been cancelled or postponed i am planning on using a small Denver furnace to fill small orders. I have been having reliability issues with MDRs sometimes failing off and worse sometimes failing on. Considering changing my MDR with a solid state relay.

Interested in whether anyone has done this and what experience they have had. Is it a simple operation and has it worked well? A Watlow representative has suggested a din na mite relay. Thank you for any input. Hunkering down in Kansas.
Reply With Quote
  #2  
Old 03-22-2020, 07:37 PM
Rick Wilton Rick Wilton is offline
Registered User
 
Join Date: Oct 2005
Location: Calgary, Alberta Canada
Posts: 220
Rick Wilton is on a distinguished road
don't buy the really cheap ssr's from Amazon. They will melt down, they are NOT designed for anything close to their stated ratings. I thought I was saving some good money buying "direct from a manufacturer" and quickly (3 months) found out they were crap and dangerous.
Reply With Quote
  #3  
Old 03-22-2020, 07:49 PM
Cecil McKenzie Cecil McKenzie is offline
Registered User
 
Join Date: Feb 2011
Location: Emporia, KS
Posts: 499
Cecil McKenzie is on a distinguished road
Thanks i was thinking about Watlow equipment.
Reply With Quote
  #4  
Old 03-22-2020, 10:06 PM
Sky Campbell's Avatar
Sky Campbell Sky Campbell is offline
Registered User
 
Join Date: May 2002
Location: Gainesville FL
Posts: 1,007
Sky Campbell is on a distinguished road
Ive never seen a mdr fail in the on position. Knowing how they work you would understand how thatís impossible unless you lay it on its side or hold it upside down. I donít think you can find anyone that would consider a ssr to be more reliable then a mdr. Maybe someone will prove me wrong but I highly doubt it.

That said I would use mdr relays for my positive cutoff and a scr to control my power. The scr if tuned correctly (reducing the gain, using soft start and only delivering as much power needed) can possibly double the life of wire elements.
Reply With Quote
  #5  
Old 03-23-2020, 07:17 AM
Pete VanderLaan's Avatar
Pete VanderLaan Pete VanderLaan is offline
The Old Gaffer
 
Join Date: Apr 2002
Location: Chocorua New Hampshire
Posts: 21,933
Pete VanderLaan is on a distinguished road
I've never seen an MDR fail at "On" either but I have seen them fail in that they shut down in the on position and close, never achieving the temperature needed for the program. It's the solenoid that gave the trouble, not the mercury portion.

Mechanical relays indeed will fail at on.

Safety issues on an MDR would not keep me up at night.
__________________
Where are we going and why am I in this basket?
Reply With Quote
  #6  
Old 03-23-2020, 08:35 AM
Brian Graham's Avatar
Brian Graham Brian Graham is offline
Registered Abuser
 
Join Date: Mar 2004
Location: Akron - Ohio
Posts: 540
Brian Graham is on a distinguished road
Din-a-mites are great- there are always a ton of them on ebay - You need to have the correct dc milivolt signal available from your controller though.
__________________
The revolution will not be televised.
Reply With Quote
  #7  
Old 03-23-2020, 10:44 AM
Sky Campbell's Avatar
Sky Campbell Sky Campbell is offline
Registered User
 
Join Date: May 2002
Location: Gainesville FL
Posts: 1,007
Sky Campbell is on a distinguished road
Quote:
Originally Posted by Brian Graham View Post
Din-a-mites are great- there are always a ton of them on ebay - You need to have the correct dc milivolt signal available from your controller though.
I think your confusing things or maybe Iíam. I know din-a-mite as producers of scr controllers not ssr controllers. A scr will require a variable miliamp input and not sure if anything uses a milivolt input.
Reply With Quote
  #8  
Old 03-23-2020, 10:49 AM
Sky Campbell's Avatar
Sky Campbell Sky Campbell is offline
Registered User
 
Join Date: May 2002
Location: Gainesville FL
Posts: 1,007
Sky Campbell is on a distinguished road
I guess I should google before talking. There are some controllers that need a milivolt signal but I personally have never seen or heard of one.
Reply With Quote
  #9  
Old 03-23-2020, 12:36 PM
Cecil McKenzie Cecil McKenzie is offline
Registered User
 
Join Date: Feb 2011
Location: Emporia, KS
Posts: 499
Cecil McKenzie is on a distinguished road
In my experience mercury relays have always failed on. I have melted paperweights and multiple vases melted together as evidence. When i started using my small Denver unit I had a couple failures with the MDRs failing in the off position which surprised me . After I started my furnace this year it ran fine then failed in off position. I could tap the relay and it would work again but then fail again. I replaced it with a relay I bought 8 years ago. It was different from many I had used in that it had brass bars connecting the two sides of the coils top and bottom. The manufacturer said this was to make them synchronized.

i was pleased since it ran much quieter than the old one. About 5 days later i noticed the furnace was at 1972 F when it said it was holding at 1950F. I am pretty sure it had been higher and then become unstuck.

When I talked to Denver they said that they thought solid state relays always stick on. I talked to Brice recently because I knew he used solid state relays. He said he though his have failed sometimes in the on position and sometimes in the off. Denver suggested a fail safe of some type to keep furnace from over heating.

These considerations have prompted me to seek advice from this board.
Reply With Quote
  #10  
Old 03-23-2020, 12:50 PM
Brian Graham's Avatar
Brian Graham Brian Graham is offline
Registered Abuser
 
Join Date: Mar 2004
Location: Akron - Ohio
Posts: 540
Brian Graham is on a distinguished road
Sky - I may be wrong - maybe it is just switched dc. I would have to go look at them in my panels. I have always run Watlow controllers as well - old series 96 and a few EZ Zone PM's. I agree that SCR's will make wire elements last longer because they soft start.
__________________
The revolution will not be televised.
Reply With Quote
  #11  
Old 03-23-2020, 01:59 PM
Shawn Everette Shawn Everette is offline
Registered User
 
Join Date: Mar 2013
Location: Indianapolis, IN
Posts: 585
Shawn Everette is on a distinguished road
I too have had MDR's fail on. An SCR too, but that was on finicky control system.

SCR is probably going to give you the longest element life, but may be harder to source, and probably more expensive as you up the amps.

SSR is probably going to be the cheapest option of those offered.

Personally I'm still on mechanical, the metronome click lets me know it's working without looking at it, and I can usually hear when it's on it's way out. I've also got 24 of them laying around, so it's the free option.
Reply With Quote
  #12  
Old 03-23-2020, 02:41 PM
Sky Campbell's Avatar
Sky Campbell Sky Campbell is offline
Registered User
 
Join Date: May 2002
Location: Gainesville FL
Posts: 1,007
Sky Campbell is on a distinguished road
Quote:
Originally Posted by Cecil McKenzie View Post
In my experience mercury relays have always failed on. I have melted paperweights and multiple vases melted together as evidence. When i started using my small Denver unit I had a couple failures with the MDRs failing in the off position which surprised me . After I started my furnace this year it ran fine then failed in off position. I could tap the relay and it would work again but then fail again. I replaced it with a relay I bought 8 years ago. It was different from many I had used in that it had brass bars connecting the two sides of the coils top and bottom. The manufacturer said this was to make them synchronized.

i was pleased since it ran much quieter than the old one. About 5 days later i noticed the furnace was at 1972 F when it said it was holding at 1950F. I am pretty sure it had been higher and then become unstuck.

When I talked to Denver they said that they thought solid state relays always stick on. I talked to Brice recently because I knew he used solid state relays. He said he though his have failed sometimes in the on position and sometimes in the off. Denver suggested a fail safe of some type to keep furnace from over heating.

These considerations have prompted me to seek advice from this board.

The only possible explanation for a mdr to fail on would be if you used a normally closed relay. That is the power flows through the relay until it is energized then the connection is cut.
Denver uses normally open relays as we all should for heating applications.
Understand how a mdr works. It is a tube with mercury inside. There are contacts at the top and bottom when it is energized a plunger is forced into the liquid displaced to make the connection. There is no arching and no contacts to wear out. It is in theory impossible to stick in the on position. They are rated in the millions of cycles and are the most reliable type relay you can use.

Solid state relays have a tenancy to fail and short on the output causing the heater to stay on as the circuit is welded together.
Attached Images
File Type: jpg 98AC33BF-999F-4568-9960-B3E207479DD9.jpg (95.0 KB, 9 views)

Last edited by Sky Campbell; 03-23-2020 at 04:45 PM. Reason: Backasswards
Reply With Quote
  #13  
Old 03-23-2020, 02:52 PM
Sky Campbell's Avatar
Sky Campbell Sky Campbell is offline
Registered User
 
Join Date: May 2002
Location: Gainesville FL
Posts: 1,007
Sky Campbell is on a distinguished road
The Idea a normally open, properly mounted MDR will fail and melt down your work isn’t happening. Your controller on the other hand can fail and continue to deliver power to the mdr even when it’s not called for.

I’m not trying to be a smart ass. Please don’t think anything I’m saying as being disrespectful or dismissing anyone’s experience. I know freak accidents happen but usually with closer examination there will be an answer.

Last edited by Sky Campbell; 03-23-2020 at 04:46 PM. Reason: Backasswards again
Reply With Quote
  #14  
Old 03-23-2020, 04:10 PM
Cecil McKenzie Cecil McKenzie is offline
Registered User
 
Join Date: Feb 2011
Location: Emporia, KS
Posts: 499
Cecil McKenzie is on a distinguished road
Sky no worries. i know the literature says the MDRs fail open rather than closed, i use MDRS that are normally open. On several occasions I have had melt downs in my anneallers. I changed the MDR and everything was fine. I have also experienced touching an element when the controller was off and received a 120 volt shock. I took this to mean that one side of the relay was closed allowing me to get shocked. The elements were not hot as per temperature but were energized by one side of the relay. Now you say that is not possible but in my case it seemed very possible.

Be that as may I am trying to find something that will work better for me.

I have been reading some about SSRs on line. One page said
mdrs are not allowed in many countries now and wonder what some other countries are using instead of MDRs,
https://www.process-heating.com/arti...mercury-relays

Still trying to figure this out. Appreciate all input.
Reply With Quote
  #15  
Old 03-23-2020, 04:53 PM
Shawn Everette Shawn Everette is offline
Registered User
 
Join Date: Mar 2013
Location: Indianapolis, IN
Posts: 585
Shawn Everette is on a distinguished road
I don't doubt the theory behind MDR's not melt down, but I've experienced the same kiln, with 2 different MDR's go thermo nuke. Relay was non functional after that, nothing odd coming from the controller, simple swap fixed all issues. Seen enough shorts instaweld metal to believe that one could fuse the plunger open in non ideal circumstances. Whether or not that was the fault of the relay could be debated.
Reply With Quote
  #16  
Old 03-23-2020, 06:30 PM
Steve Beckwith Steve Beckwith is offline
Registered User
 
Join Date: Feb 2007
Location: Cocoa Beach, Florida
Posts: 94
Steve Beckwith is on a distinguished road
I ran a Denver furnace and on at least two occasions I had an MDR fail in the on position. It would be discovered when I made contact with the metal frame with the pipe while gathering. Not a full voltage dose but enough to give a nice tickle. I was running them at the upper range of their amp rating. If I recall, I had problems with a 40 amp relay. I switched to a 60 amp and had no further problems.
Reply With Quote
  #17  
Old 03-23-2020, 06:35 PM
Pete VanderLaan's Avatar
Pete VanderLaan Pete VanderLaan is offline
The Old Gaffer
 
Join Date: Apr 2002
Location: Chocorua New Hampshire
Posts: 21,933
Pete VanderLaan is on a distinguished road
well, everything works well until it doesn't.
__________________
Where are we going and why am I in this basket?
Reply With Quote
  #18  
Old 03-23-2020, 07:11 PM
Cecil McKenzie Cecil McKenzie is offline
Registered User
 
Join Date: Feb 2011
Location: Emporia, KS
Posts: 499
Cecil McKenzie is on a distinguished road
Steve Beckwith
"I ran a Denver furnace and on at least two occasions I had an MDR fail in the on position. It would be discovered when I made contact with the metal frame with the pipe while gathering. Not a full voltage dose but enough to give a nice tickle. I was running them at the upper range of their amp rating. If I recall, I had problems with a 40 amp relay. I switched to a 60 amp and had no further problems."
Steve i can recall noticing that the red light that indicated the elements were on started to come on while the door was open. The furnace had been running normally as far as heating but I figured that the side of the relay that runs the clock and the warning light had failed in the on or closed position. I remember thinkng that when the furnace was in that condition you might get shocked by 120 ac even though I never did. Maybe I should get a higher rated MDR. The salesman for Watlow thought SSR s are appropriate for heating applications. Thanks for your input.
Reply With Quote
  #19  
Old 03-23-2020, 07:52 PM
Shawn Everette Shawn Everette is offline
Registered User
 
Join Date: Mar 2013
Location: Indianapolis, IN
Posts: 585
Shawn Everette is on a distinguished road
I know the tickle of a element, but I don't get what would have caused it in your case. Even if a relay fails on it "should" be isolated enough from the frame to prevent transfer. Don't know all denver's, but the one I serviced seemed like the coil was a safe enough distance away from the glass and frame.

Then there's holding an a frayed end of an cord in the middle of rewiring while your "assistant" plugs it in. That's a good jolt
Reply With Quote
  #20  
Old 03-24-2020, 05:09 AM
Steve Beckwith Steve Beckwith is offline
Registered User
 
Join Date: Feb 2007
Location: Cocoa Beach, Florida
Posts: 94
Steve Beckwith is on a distinguished road
I always assumed that because molten glass will conduct electricity and the inside of the furnace was coated in glass from the dust from the batch while charging that is how I was able to get a poke. A couple times I used "percussive maintenance " on the MDR and it would function normally for a while.
Reply With Quote
  #21  
Old 03-24-2020, 07:00 AM
Pete VanderLaan's Avatar
Pete VanderLaan Pete VanderLaan is offline
The Old Gaffer
 
Join Date: Apr 2002
Location: Chocorua New Hampshire
Posts: 21,933
Pete VanderLaan is on a distinguished road
Electricity is always drawn to the best ground. If you stand in a puddle of water with a crackerbox welder and use it, it's quite likely to nail you despite your ground cable.

True of a furnace and its wiring as well. Years back, I had a moly element droop and contact the crucible and I did not see it. I went in with a pipe and there was no current draw. The double insulated transformer was doing its job. If I'd been in water, a different story.
I di shut down and repair the problem as soon as I saw it was there.
__________________
Where are we going and why am I in this basket?
Reply With Quote
  #22  
Old 03-24-2020, 08:37 AM
Greg Vriethoff's Avatar
Greg Vriethoff Greg Vriethoff is offline
Triggered
 
Join Date: Jan 2007
Location: Aarde
Posts: 2,218
Greg Vriethoff is on a distinguished road
Quote:
Originally Posted by Pete VanderLaan View Post
Electricity is always drawn to the best ground.
Path of least resistance.

I worked with a guy at my first metal fab job in Seattle that majored in sculpture at UW. He told me of the time he was working on a large piece outdoors in the yard where students could work on large projects. It was 20-25 in length. He hooked his buzz box at one end and tacked the corner. He moved to the other joint without moving the ground lead. He moved further away, and was then standing on damp grass. Suddenly, pow! Said he saw stars. When he came to he realized he'd wet his pants.
Reply With Quote
  #23  
Old 03-24-2020, 11:49 AM
Cecil McKenzie Cecil McKenzie is offline
Registered User
 
Join Date: Feb 2011
Location: Emporia, KS
Posts: 499
Cecil McKenzie is on a distinguished road
Talked directly with the Watlow representative. He said there was no real advantage to change to a SSR and the fact that the MDR I had installed was 8 years old may have contributed to its failure. He recommended putting a new MDR on and go from there.

He also said there is no truth to the belief that MDRs always fail open or SSRs always failing closed. So I am going to get a new MDR and trust the force. Thanks for your responses.

















ssr
Reply With Quote
  #24  
Old 03-24-2020, 12:02 PM
Pete VanderLaan's Avatar
Pete VanderLaan Pete VanderLaan is offline
The Old Gaffer
 
Join Date: Apr 2002
Location: Chocorua New Hampshire
Posts: 21,933
Pete VanderLaan is on a distinguished road
Dudley does sell MDR's
__________________
Where are we going and why am I in this basket?
Reply With Quote
  #25  
Old 03-24-2020, 12:03 PM
Pete VanderLaan's Avatar
Pete VanderLaan Pete VanderLaan is offline
The Old Gaffer
 
Join Date: Apr 2002
Location: Chocorua New Hampshire
Posts: 21,933
Pete VanderLaan is on a distinguished road
Quote:
Originally Posted by Greg Vriethoff View Post
Path of least resistance.

I worked with a guy at my first metal fab job in Seattle that majored in sculpture at UW. He told me of the time he was working on a large piece outdoors in the yard where students could work on large projects. It was 20-25 in length. He hooked his buzz box at one end and tacked the corner. He moved to the other joint without moving the ground lead. He moved further away, and was then standing on damp grass. Suddenly, pow! Said he saw stars. When he came to he realized he'd wet his pants.
*****
Thank you.
The correct term was alluding me at the moment. I too have had your friend's experience.
__________________
Where are we going and why am I in this basket?
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 07:11 PM.


All published comments within these message boards are the opinions of its contributor and does not represent
the opinion(s) of the owner(s) of this website. Please see the Terms of Use file for more details.

Books to Help Artists Avoid Online Scams: Top 10 Email Scams | Social Media Scams

Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
© CraftWEB.com. Opportunity Network. 2008. All Rights Reserved.