Hi Franklin

The Numbers looks a little off with Pb looking too small for a furnace. Here is a procedure from watlow that Ive used to manually tune.

https://cn.watlow.com/-/media/docume...pid-loops.ashx
Reply With Quote
  #27  
Old 07-19-2020, 09:47 PM
Franklin Sankar's Avatar
Franklin Sankar Franklin Sankar is offline
Registered User
 
Join Date: Apr 2002
Location: Trinidad, West Indies
Posts: 4,028
Franklin Sankar is on a distinguished road
Thanks Brian. I was using the following which I found in the watlow 93 site
I will try yours tomorrow.
Franklin

1. Apply power to the Series 93 and enter a set point. Set Operation parame- ters as follows: [``Pb] to [```1], [``rE] / [``It] to [`)00], [``rA] / [``dE] to [`)00], [``Ct] to [``%0], [`CAL] to [```0], [`AUt] to [```0].
2. Proportional Band Adjustment: Gradually increase [``Pb] until the upper display temperature stabilizes to a constant value. The process tem- perature will not be right on set point because the initial reset value is 0.00 repeats per minute. (When [``Pb] is set to 0; [``rE] / [``It] and [``rA] / [``dE] are inoperative, and the Series 93 functions as a simple on-off con- troller.) The [`HSC] parameter determines the switching differential value.
3. Reset/Integral Adjustment: Gradually increase [``rE], or decrease [``It] until the upper display temperature begins to oscillate or "hunt." Then slowly decrease [``rE] or increase [``It] until the upper display sta- bilizes again near the set point.
4. Cycle Time Adjustment: Set [``Ct] as required. Faster cycle times sometimes achieve the best system control. However, if a mechanical contac- tor or solenoid is switching power to the load, a longer cycle time may be de- sirable to minimize wear on the mechanical components. Experiment until the cycle time is consistent with the quality of control you want. [``Ct] will not appear on units with a process output.
5. Rate/Derivative Adjustment: Increase [``rA] / [``dE] to 1.00 minute. Then raise the set point by 11 to 17C, or 20 to 30F. Observe the system's approach to the set point. If the load temperature overshoots the set point, in- crease [``rA] / [``dE] to 2.00 minutes.
Raise the set point by 11 to 17C, or 20 to 30F and watch the approach to the new set point. If you increase [``rA] / [``dE] too much, the approach to the set point is very sluggish. Repeat as necessary until the system rises to the new set point without overshooting or approaching the set point too slowly.
Reply With Quote
  #28  
Old 07-20-2020, 10:21 AM
Franklin Sankar's Avatar
Franklin Sankar Franklin Sankar is offline
Registered User
 
Join Date: Apr 2002
Location: Trinidad, West Indies
Posts: 4,028
Franklin Sankar is on a distinguished road
I tried auto tune one more time and it worked.
I dropped 200 from the set point then started the auto tune and it worked like magic. I feel the next time I start up the settings will not work at start up temp but will do a work around if that happens.
I will note the parameters used so next time I will be ok.
Thanks for all the help
Franklin
Reply With Quote
  #29  
Old 07-20-2020, 10:31 AM
Franklin Sankar's Avatar
Franklin Sankar Franklin Sankar is offline
Registered User
 
Join Date: Apr 2002
Location: Trinidad, West Indies
Posts: 4,028
Franklin Sankar is on a distinguished road
P= 7 I=.1 d=.47
It will be interesting to see what happens next startup.
Franklin
Reply With Quote
  #30  
Old 07-21-2020, 08:42 PM
Brian Wong Shui Brian Wong Shui is offline
Registered User
 
Join Date: Oct 2002
Location: Atlanta, GA
Posts: 183
Brian Wong Shui is on a distinguished road
Thats great.

Next time the furnace is up, check to see how the furnace behaves when you upset it from steady state (i.e opening and closing the door when gathering glass). Look at output percentage. As soon as it detects the temperature is falling, you should see the output jump to 100% right then. It should overshoot the setpoint and then fallback to slightly under and then converge on the setpoint. The output percentage should be fairly steady once it finds the setpoint and not erratically jumping around.

If it takes too long to get back, try reducing the d a little. (You did record the values, right?). Too much d makes the system slow. Ideally you want the system slightly underdamped to critically damped. This will have the fastest response back to the setpoint.
Reply With Quote
  #31  
Old 07-22-2020, 09:46 AM
Franklin Sankar's Avatar
Franklin Sankar Franklin Sankar is offline
Registered User
 
Join Date: Apr 2002
Location: Trinidad, West Indies
Posts: 4,028
Franklin Sankar is on a distinguished road
Thanks will do. Values recorded above
Franklin
Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is Off
HTML code is Off
Forum Jump


All times are GMT -5. The time now is 11:48 AM.


All published comments within these message boards are the opinions of its contributor and does not represent
the opinion(s) of the owner(s) of this website. Please see the Terms of Use file for more details.

Books to Help Artists Avoid Online Scams: Top 10 Email Scams | Social Media Scams

Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2020, Jelsoft Enterprises Ltd.
CraftWEB.com. Opportunity Network. 2008. All Rights Reserved.